Hi all,
I have finished a PLM module and it works fine but I though for ease of my operators I wanted to operate the PLM using buttons, I have created a START, STOP, and RESET but I keep getting the following error when I activate the buttons "rtc_invalid_phase_command".
I have tried the following versions of code on the START button can anyone see what I have done wrong?
1.WriteValue "$phase_command:START", "DVSYS.322_TKS_RECIRC/XCOMMAND.F_CV" (I was wondering if I am not writing to the correct named set)
2.WriteValue "START", "DVSYS.322_TKS_RECIRC/XCOMMAND.F_CV"
I would appreciate any help or guidance you can give me.
Your logic is writing a string "START" to a number field (F_CV) of XCOMMAND, change the F_CV to A_CV in option 2.