I want to design a panel for a single VIM2 and simplex SX, with a blank 2-wide in between to put another SX in for redundancy in the future. Through conversations with some colleagues and research into the documentation, I've heard the following constraints:
I don't think these can both be true. If you put a VIM2 next to two SX which are redundant, and the active SX fails, the standby SX will not be directly next to the VIM2, so according to point 1 the VIM2 will not communicate with the redundant SX. So then if you put a VIM2 directly to the left of each SX, now the SX can no longer be redundant according to point 2. So one of these must be wrong.
Question 1: How do you configure a VIM2 with redundant SX in a panel?
Question 2: If the redundant SX from question 1 is switched to a simplex, and the controller which is removed is replaced with an empty 2-wide, can the controller still communicate both with the VIM2 and with an 8-wide with other I/O cards?
I appreciate any insight, thanks!
Andre Dicaire
In reply to Andre Dicaire: