Hi, we are using deltav 11.3.1 with PCSD modules for PID control. The AO function block is connected to a HART enabled channel connected to an ABB EDP300 smart positioner. The module AO/XD_SCALE was set at 0-100 no units but since connecting with the EDP300, is being over-written online with 4-20 mA. Im unable to change the units and scale upper and lower values in the EDP300 to 0-100. As a result, the vertical bar on the PCSD Loop faceplate that represents output goes full scale when the output exceeds 20, therefore no visualisation of 20-100 output range.
Has anyone successfully integrated an ABB EDP300 smart positioner with a DeltaV PCSD module?
I don't think L_type option can be used as it is the AO block we are talking about, also in IO_OUT for an AO block, you do not have the option of using any other parameter field except OUT. Just try putting in % in the XD scale units instead of "no units" in offline mode and download and see if that works by checking in online mode if the XD scale is still changing to 4-20 or not, At times "No units does not work" along with HART positioners. if it still shows 4-20 mA, Try changing the XD scale in online mode to 0 to 100, you can do that by taking the AO block in Manual mode (You can change the XD scale of AO block in manual mode as in CAS mode of AO block it doesn't allow that-enable manual mode for AO block if not enabled in offline and download before changing the AO XD scale in online mode), Put the AO block back in CAS Mode, If none of this work, change the AO channel type from HART channel to non HART so that you get the value in 0 to 100% and ask ABB on how to change the HART Output in the positioner from 4 to 20 to 0 to 100%. If you have the DD files uploaded, you should be able to do that through AMS itself.
In reply to Stuart Jolley:
In reply to Matt Stoner:
In reply to James Beall: