Hi all,
We have a particular VFD on Ethernet/IP that keeps faulting out on network timeouts = MODBAD status in DeltaV. While we are troubleshooting the network/hardware issues, I would like to know if there is any way to ignore the network fault so that our sequences keep rolling through the 1-2 second faults.
Thanks in advanced.
Update from Emerson Exchange 365 foxriver Not sure how to ignore the network fault. But I have experienced similar communication issues with devices on a VIM1 card. In the port settings you can adjust the number of retries as well as the timeout time. If you increase one or both of these it will take longer to declare a fault on that port, and may help you ride through the issue. View online You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here. Flag this post as spam/abuse.
Not sure how to ignore the network fault. But I have experienced similar communication issues with devices on a VIM1 card. In the port settings you can adjust the number of retries as well as the timeout time. If you increase one or both of these it will take longer to declare a fault on that port, and may help you ride through the issue.
View online
You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here.