Have existing control modules that are doing a bunch of environmental averaging. They are all pathed to separate modules. I am wanting to create a composite & a custom faceplate to display all of them together. Not sure exactly how to write to the external path in a parameter block from a Calc Block.
So what I am wanting to do is enter a tag# 123456 Then use a calc block to write that string for the 7 individual external references that I need for the associated tag. Ex.
AI-12345/PV.CV
AI-12345-B1S/PV.CV
AI-12345-B1M/PV.CV
AI-12345-B15M/PV.CV
AI-12345-B1H/PV.CV
ETC. I have to do this for 180+ modules and I know I can do it with a bulkedit, but want to create a composite so I can class it & they be the same for all.
I have to code to make the string and I can write it to a parameter as the string value. But I can't figure out how to path that string to the parameter external reference so it will go get the right data. Thanks in advance for your help.
In reply to MCrisler:
Thanks for your help, that was exactly what I needed.
my calc block has the following line of code that wrote to a input parameter set as a dynamic reference. Then I tied an output parameter to the input parameter so I could see the live value instead of clicking the block. Thank you sir.
'^/PARAM1.$REF' := "//AI-" + '^/TAG.CV' + "-B15S/15SEC_AVG.CV";
I just replicated this line with the additional tag syntax and it works great. Now I just have to when I update the Tag.CV it propagates down. This will make the class & dynamo a lot easier without changing any of the calc modules that environmental references.
Much appreciated.