When I try to login to DeltaV remotely using a resolutin of 1920x1200 it shows operate fills part of the screen on the right like its running a 1680x1050 while at 1920x1200 resolution however we are running that same resolution on the desktops in the plant and everything looks fine. Any ideas on how to fix it?
The reason I want to do this is that when I work on the graphics here and look at them in the plant they look different. I develop them on 1680x1050 since thast the max resolution I can run operate in Run mode while remoted in.
In DeltaV Operate Configure Mode:
Click on the DeltaV User Settings button on the DeltaV Edit Toolbar
Ensure the Bypass option is NOT selected
Then make sure that the layout files (copy them) from the desktop machines you referenced are also on the term server machine