Our system had only DD files for Invensys SRD991 Rev 9 and 16. I have a new device with Rev 18 to install
Over the weekend we have installed DD files on AMS and EWS(V11) from this link on fieldbus.org site:
http://www.fieldbus.org/index.php?option=com_mtree&task=viewlink&link_id=1736&ffbstatus=Registered&Itemid=324
The device was commissioned successfully and you can see the methods ,process variable and configuration setup on AMS and EWS by right click menu.
However I could not download!!. The download error log reads
The troubleshooting I carried out
I discovered that of the three items checked for download: Fieldbus device 03FCV201, Fieldbus Alarms, and SRD991 Analog Output blocks the last one which is the AO block would not download.
I tried to upload function blocks from the field device, all uploaded except the : SRD991_AO-62/041770 SHED_OPT CV1
I checked the control module on Studio and saw that the AO block permitted mode, target mode and Normal mode are different from the fieldbus device viewing it from configuration setup. I tried to change these fieldbus device configuration setup AO block modes to match the control studio but the AOTB Mode was returning error. I could change the modes of Resource block , DI Transducer and DO transducer blocks from configuration setup but AO block proves sturbborn
Advise me
Emerson has sent me a link for DD files earlier I want to try that one. It has install.ini and .fhx in it unlike the one I have used from fieldbus site. Does that make sense?? If you have any help document on Un-installing DD files from AMS and EWS I would appreciate it.
If the problem is not DD file installed from fieldbus.org site what else could be the issue
Please save me urgently