Dear My friends
I got this report from one of our clients :
" After rebooting one of the OWS which was hanged , the DeltaV system time changed to 30 min back and caused a total shutdown. this issue happens 2 times from same point (same OWS) during this month "
The masted Time sync is set to Pro+
Now I want to know why it happened and what should I do for survey and remedy.?
Thank you in advanced for any data
Best Regards
Jefry
In reply to Alexandre Peixoto:
In reply to damer.j1975:
What antivirus solution are you using on the workstations? Are your virus definitions up to date? I think you may be associating one thing (Windows system time change on OWS) with an unrelated event (operator stations become unresponsive). As Alexandre pointed out, opening a call with GSC is a must. Unless you configured the "stopped" OWS to be the Master Time Server in the DeltaV configuration, then all nodes will synchronize with the ProPlus. Rebooting a machine that is not the authoritative time server does not cause a DeltaV system time change.