Hi My Name is Sami ...within the span of 22 days we observed same issue that all pid loops relates to pressure and flow goes open wrt there acting where as temperature and level dont show a change due to slow response
We have two controllers
Controller 2 ( load percentage 14) related cards AO are working fi9 and found no change
Controller 1 (load percentage (23%) related cards AO are problamatic but dere is no system issue as per the events ( Manually done the cards redundancy check and controller redundancy check and all are working fi9)
(Issue time span is to0 small (10-20 seconds) that when reach to field everything get normal and only trend help to identify loops )
Remedies which i have done
Unresolved issues resolved ( alarms which were not configured)
power supply check ( and its redundancy) = All Ok
bay supply voltage check
If same thing occur again then what next i have to do ....Problem is critical for our plant as it may create column pressure xv pop up yet i m observing it on regular basis
In reply to Maarten van der Waal:
In reply to DBacker:
Mr DBacker thank you for the reply...yes i have trended it is matching for instance if it is vaccum loop the sudden problem which occur made that controller to Failed to Open PV showing the vaccum going towards coarse yet sp remains the same ..dese type of acivity happened in pressured and flow looops as both loops have fast response nd did not find any change in level and temperature loops...from my end i have checked ( written in question) nd yet observing on daily basis...all in all ... all control valves acted as failure and AO have redundancy as well ...