Hi,
Can I use DeltaV SIS logic solver as Analog Output?
In reply to GeloCortez:
As Roshan pointed out, the AO on the DeltaV SIS is a two-state output, low (4mA) and high (20mA) with HART; the AO does not modulate and you therefore cannot use it for regulatory control.
In reply to MC_Chow:
Andre Dicaire
In reply to Andre Dicaire:
Bill Reeson
Global Project Pursuit & Strategic Account Manager | ASCO
Emerson
T +1 973 966 2097 | M +1 973 495 8561
Bill.Reeson@Emerson.com
In reply to Bill Reeson: