• Not Answered

Entering charge weight set points into faceplate

HI,

I have been asked if it is possible for the operator to have to enter the same figure twice into the faceplate for charge weight set points before it is accepted. 

From a safety point of view this would reduce the amount of errors but I'm not sure this is possible?

any help is greatly appreciated.

Thank you in advance.

Lee Wren

2 Replies

  • Hi Lee,

    yes it´s possible you just have to make your own faceplate and do some programming.

    Program it like when you have to add a password at a internet site, you have two fields first insert password the second field is confirm password, if they don´t match it won´t work.

    Or you could use the DV built in Electronic signature function...

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to Niklas Flykt:

    great news Niklas thankyou, doing my own programming sounds a little daunting , is the electronic signature function explained in Books Online?