In a brownfield project, we have serial devices sending the modbus data to DeltaV. The serial IO list contains list of 16 bit registers coming to DeltaV (e.g. address range R30001 to R30100).
There is also a column called 'SIGNED' in the customer supplied data where data is 'TRUE or FALSE for a particular 16 bit integer tag.
The problem is the 16 bit integers are laid out such that they are not grouped for signed and usnsigned integers (not contageous). e.g. R30001 to R30010 are SIGNED registers, R30011 to R30015 are UNSIGNED etc...
This if we have to implement in DeltaV; we have to create a seperate 'Dataset' for each block of Contageous Signed or Unsigned registers thus massively increasing the number of datasets per port. (>16).
The customer has said they can not change the data mapping in the field as it is a brownfield project and third party running are very old.
Question is-
Is there any way in DeltaV where we can read the contageous registers (say R30001 to R30100) in one dataset of data type '16 bit unsigned' integers and convert the unsigned tags to 'Signed 16 bit registers using some CALC logic or any algorithm?
Has this been done by anybody in the previous projects or any idea how to implement this logic to convert unsigned integer to signed integer in DeltaV?
Please advise.
Thanks and Regards,
Abhijit Joshi
In reply to AbhiJos: