Good Evening ;
helllo every one;
If you allow I have some questions for you;
currently working on a project with the deltav system and I must establish a fieldbus communication with different brand of instruments for example, has a krohne brand flowmeter IFC 300 and a level transmitter and even for OPTIWVE 7300; I made several research on the Emerson website but I could not find “ file.fhx ” so I can add at deltav explorer and about IFC300 I found three files, but the latest revision is compatible with version 10.3 is that file that will work with deltav 11.3.
Thank you very much.
Best regards.
Butler faith.
It's not a bad practice to search the Emerson site for device files, but you can always get a functioning DD for any device that has passed interoperability testing from the fieldbus.org website. Sometimes I've even found Emerson device files here before they appeared on the DeltaV website.
DeltaV versions 10 and higher have all passed host registration to the highest available level of compliance, and so have been tested to support the device files you download from there. It just may be that some nuances of the presentation have not been configured to display, for example a custom icon for the instrument.