I am putting together a DeltaV Batch system in V12.3 using PCSD. I have a unit with more than 16 defined "Hold" conditions (22). The problem is that the PCSD Common Hold Monitor composite (C_FAIL_MON120) only allows for 16 conditions.
How can I properly add the additional HM conditions and get them to appear on the Unit's HM detail tab (or an additional tab)?
Thanks,
Dave,
First you will need to convert the FAIL_MONITOR to embedded. To do this right click on the composite shown below.
Now you are able to edit the FAIL_MONITOR composite and add the HM17-xx conditions, add the HM_17-xx boolean parameters, and also edit the CND_DESC action block if you want HM descriptions to insert Alias resolution values for the HM17-xx conditions.
Now you have a choice, you will need to either create a new composite for the HOLD_ENG composite or drill down into the composite and override the HM1 and HM2 expressions.
The PCSD_UM_120_DT display will support up to 64 HM conditions without modification.
If you have issues or further questions on this you can email me directly at matt.stoner@emerson.com.
Regards,
Matt