When loading graphics, we often get the error "The item definition does not exist within the servers address space" for several modules. It is usually for PID loops which have the OUT.F_CV parameter. In addition, the graphics containing these modules show purple initially like the system can't find the information. Once the errors are skipped, the graphic works fine and the modules are accessible with no issues. If we switch to another graphic and come right back, the error does not occur, but if the graphic is not on the screen for a few minutes and then is accessed again, the error occurs again. One time we may get the error for 6 modules, the next time it may only be for three. It seems to occur on workstations differently. One workstation is located in the same area as the ProPlus workstation and it rarely has an issue. Another workstation located in the control room (300 ft and on a secondary hub) has the issue more often.
It seems like the graphic can't access the database fast enough to get all the data before it throws an error. Anyone else have this issue or thoughts on how to resolve?
In reply to Steven Estes: