I want to achieve a set up whereby an operator has to verify when an alarm is suppressed. So far we have set up a policy in electronic signatures using the opsup parameter. This function works when suppressing alarms from the detail faceplate by checking the appropriate box however, an operator can still suppress an alarm that's active in the faceplate or in the alarm lists.
I have found in DeltaV Operate Configure with any faceplate open or the Alarm List (from DVCtrlAlmSum1), right clicking in the Ack/Message field/or alarm List, using pop up menu and selecting 'properties...DeltaV.DVAlarmSummary Object' a new window opens 'DeltaV Alarm Summary Configuration', selecting the last tab 'Actions' shows the actions availble from right-click context menu.
Finally, my question is de-selecting Suppress/unsuppressed an alarm the way to go or is there a downfall to implemeting this or another tried and tested method for this.
Thanks,
I assume by verify you mean they need to push a second "OK" button to confirm they wish to suppress the alarm. I don't think I have ever done that for an alarm. I would think if they clicked the faceplate, then the detail faceplate, and then the alarm suppress button they would always click the last "OK" button at that point. Anyway, you have the correct idea that you would need to place a wrapper on all the locations the alarm can be suppressed for this to work everywhere.
As for other options, I typically implement this using security keys and the suppression timer. If the alarm is used as a Safety IPL then I give it a security setting such that it can only be suppressed by a Supervisor login. Then based on priority and site alarm policy I set the suppression timeout. Any HI priority or Safety based alarm I set the timeout to one shift, this way it will re-alarm and need to be suppressed each shift by each operator/supervisor. It sounds a little annoying but it should be annoying so they get it fixed.
I also set the rest of the suppression timeouts to something longer (2 wks to 30 days) so we remember that it is suppressed and not just forget about it forever. I would suggest anything suppressed longer than a month or two likely should not be an alarm. You can set the timeout based on priority or determine it for each alarm in alarm rationalization.