Dear all,
I am new to DeltaV. I would like to see if there are any guidelines/check lists available in this forum that discuss the safety checks to consider when we download control modules in DeltaV DCS in a live plant? Any suggestions would be greatly appreciated.
Thank you,
From Books On Line article 'Downloading Data':
www3.emersonprocess.com/.../c_download_data.html
"A download temporarily disrupts the part of the operation of the controller or workstation that is being downloaded. Care must be taken to determine if the process can withstand this temporary disruption. To ensure the safety of the process, it might be necessary to delay the download of the configuration changes until the process can be shut down. To minimize the effects of such disruption, it is recommended that only those parts of the configuration that have changed be downloaded. This is particularly important in the case of controllers."
This article and sub-articles provide a very thorough description of how specific downloads affect the system.
In general, you should expect a download to be disruptive to the system being downloaded and then any systems that have dependency on that system.
There are design principles that can be employed to mitigate cascaded disruption, but it must be planned well in advance.