Potential OPC Problem/Question

Please find a transcript of our system report below. Appreciate all feedback. Thank You.

1. Symptoms

  • OPC data is not communicating or receiving with My Application Software.
  • My Application Software (customize software) operating normal with other applications, and no abnormal symptoms has been seen till now with any other software or system.
  • If we exit from and run the My Application Software again then we receive the OPC data’s properly.
  • We confirm that, in program, OPC data is lost when Error is identified in Event Log 
  • Please check the below window event viewer captured error.

2. Window Event Viewer, Captured Event Logs 

1) Application Error

* English Translation in Detail

Faulting Application Name: o_server.exe, Verson: 5.60.54.763, Timestamp: 0x52260a1e

Faulting Module Name: MSVCR100.dll, 버전: 10.0.40219.325, Timestamp: 0x4df2be1e

Exception Code: 0xc0000005

Fault Offset: 0x00001ed7

Faulting Process ID: 0x684

Faulting Application Start time: 0x01cfa2504b9e2c10

Faulting Application Path: D:\RBMnet\RBMSuite\Sys\o_server.exe

Faulting Module Path: C:\Windows\system32\MSVCR100.dll

Report ID: 2182c253-0f32-11e4-8bb1-d05099114ad8

2) Windows Error Reporting

* English Translation in Detail

Fault bucket , type 0

Event Name: APPCRASH

Response: Not available

Cab ID: 0

Problem signature:

P1: o_server.exe

P2: 5.60.54.763

P3: 52260a1e

P4: MSVCR100.dll

P5: 10.0.40219.325

P6: 4df2be1e

P7: c0000005

P8: 00001ed7

P9: 

P10: 

Attached Files:

C:\Users\CSISERVERS\AppData\Local\Temp\WEREFDA.tmp.appcompat.txt

C:\Users\CSISERVERS\AppData\Local\Temp\WERF2D7.tmp.WERInternalMetadata.xml

C:\Users\CSISERVERS\AppData\Local\Temp\WERF2D8.tmp.hdmp

C:\Users\CSISERVERS\AppData\Local\Temp\WERFCA9.tmp.mdmp

This file is available at.

C:\ProgramData\Microsoft\Windows\WER\ReportQueue\AppCrash_o_server.exe_ceda1d4b76c61a568b1432d47305c951e206b45_cab_15affd13

Anaylsis Symbol: 

Rechecking for solution: 0

Report ID: 2182c253-0f32-11e4-8bb1-d05099114ad8

Report Status: 4

3) Csimtdbmgr

* English Translation in Detail

The description for Event ID 2 from source Csimtdbmgr cannot be found. Either the component that raises this event is not installed on your local computer or the installation is corrupted. You can install or repair the component on the local computer.

If the event originated on another computer, the display information had to be saved with the event

The following information was included with the event:

thread(3048): [LC1209] Error - MTDBMgr.cpp (-5111) serverHandler() - Connection failed with Dserver-deokso; Value: -5111  network error code: 10054

요소가 없습니다

4) Windows Error Reporting

* English Translation in Detail

Fault bucket , type 0

Event Name: APPCRASH

Response: Not available

Cab ID: 0

Problem signature:

P1: o_server.exe

P2: 5.60.54.763

P3: 52260a1e

P4: MSVCR100.dll

P5: 10.0.40219.325

P6: 4df2be1e

P7: c0000005

P8: 00001ed7

P9: 

P10: 

Attached files:

C:\Users\CSISERVERS\AppData\Local\Temp\WEREFDA.tmp.appcompat.txt

C:\Users\CSISERVERS\AppData\Local\Temp\WERF2D7.tmp.WERInternalMetadata.xml

C:\Users\CSISERVERS\AppData\Local\Temp\WERF2D8.tmp.hdmp

C:\Users\CSISERVERS\AppData\Local\Temp\WERFCA9.tmp.mdmp

These files may be available here.

C:\ProgramData\Microsoft\Windows\WER\ReportQueue\AppCrash_o_server.exe_ceda1d4b76c61a568b1432d47305c951e206b45_cab_15affd13

Analysis symbol: 

Rechecking for solution: 0

Report ID: 2182c253-0f32-11e4-8bb1-d05099114ad8

Report Status: 0

5) “CsiO_Server” 

* English Translation in Detail

The description for Event ID 2 from source CsiO_Server cannot be found. Either the component that raises this event is not installed on your local computer or the installation is corrupted. You can install or repair the component on the local computer.

If the event originated on another computer, the display information had to be saved with the event

The following information was included with the event:

thread(4672): [LC0059] Informational - GuiThread.cpp (0) Logging thresholds:

'File' @ 'INFORM'

'Application Log' @ 'ERROR'

'Console' @ 'NONE'

요소가 없습니다

3. Recent Status

1) Confirmed that, event log is visible before the communication is broken.

2) When we exit from program (My Application Software) and re-start, then My Application Software is receiving the OPC data, it means that OPC and My Application Software is communicating between them well.

3) This error occurs when the connection between the OPC is not broken, and seems to have the restored together, My Application Software attempts to forcibly reconnect but no response.
To get response we must restart the program.

4) Window and program reinstalled, data request time is reconfigured (change the data requested time to longer) but the situation is same

5) Most of time it occur between 10 hours, but we confirmed that this occurs at approximate when it is more than 24 hours.

4. System Information

1) PC : I7 – 4770 CPU, 8GB Ram

2) OS : Windows 7 Professional 64Bit (Korea)

3) MHM version : 5.60

4) CSI 6500 Firmware Version : 3.20d

5) Application Program Tool : LabVIEW 2013

4 Replies

  • Whenever client/server communications are in question, the first test is to use another client and see if you can reproduce the results. If you cannot, then it might indicate a problem with your client.  In the error logs you have presented, the visual C component (MSVCR100.dll) of the client application is throwing the error, again suggesting a client problem.  

    The network error code 10054 indicates the server is resetting the connection.  Have you checked the even log on the server (Dserver-deokso)?

  • In reply to Youssef.El-Bahtimy:

    Thank You for reply. From recent situation it is a little bit difficult to install a separate client PC to conduct a test, but I will format the PC and reinstall the window to conduct the test I am trying to take below actions for conducting test, so requesting to guide me regarding this problem and if possible please let me know the solution. First of all I will reinstall the MSVCR100.dll file. Regarding Network code 10054, I was able to find the relevant information at below link. http://support.microsoft.com/kb/981344/en-us “An application may receive the 10054 error when the application receives data from a connection on a computer that is running Windows 7 or Windows Server 2008 R2 if a TDI filter driver is installed. For example, a TDI filter driver is installed when you install McAfee VirusScan” Have you ever experience a similar scenario with OPC program (such as TDI filter driver is installed with MHM SW)., if yes then please let me know the solution. In addition, I would like to know, does OS language make any problem, currently we are conducting test on Korea language OS Finally, I will try to display the data via OPC Browser to check whether the data is broken, I would like to know does it help me to resolve the problem. Again Thanks for your reply and hope to get support.
  • In reply to Youssef.El-Bahtimy:

    Thank You for reply.

    From recent situation it is a little bit difficult to install a separate client PC to conduct a test, but I will format the PC and reinstall the window to conduct the test

    I am trying to take below actions for conducting test, so requesting to guide me regarding this problem and if possible please let me know the solution.

    First of all I will reinstall the MSVCR100.dll file.

    Regarding Network code 10054, I was able to find the relevant information at below link.

    support.microsoft.com/.../en-us

    “An application may receive the 10054 error when the application receives data from a connection on a computer that is running Windows 7 or Windows Server 2008 R2 if a TDI filter driver is installed. For example, a TDI filter driver is installed when you install McAfee VirusScan”

    Have you ever experience a similar scenario with OPC program (such as TDI filter driver is installed with MHM SW)., if yes then please let me know the solution.

    In addition, I would like to know, does OS language make any problem, currently we are conducting test on Korea language OS

    Finally, I will try to display the data via OPC Browser to check whether the data is broken, I would like to know does it help me to resolve the problem.

    Again Thanks for your reply and hope to get support.

  • In reply to ASJ:

    Sorry, when I said use another client, I meant client software application; you can use the same PC, just a different application. OSI's PI OPC Tool is an excellent test client, but you also try Matrikon OPC explorer, both can be procured easily.

    If you've installed DeltaV OPC Remote software on the client PC (you would have to in order to make it talk), make sure you are using the correct version to account for the 64-bit client PC per the follwoing article NK-1300-0140.

    www3.emersonprocess.com/.../carticle.asp

    The following article NK-1200-0286 describes how OPC DA clients can experience memory leaks causing failure over time.  This may describe the symptom you are seeing of failure after 24 hours of run time.

    www3.emersonprocess.com/.../carticle.asp