Multimonitor Pop-up Position

Hi,

I have a quad monitor V9.3 system, can anyone help with the way to set the position of the pop-ups?

The faceplates & detail displays work as expected and pop up in the last position everything OK. It is the operator set-point data input fields which pop up a dialogue box, always appear on the primary display rather then the display they have been clicked on.

The pop-ups are generated via an "on click" script which runs the following procedure: GetPBLFormAlphaNum

Is there a setting somewhere I am missing to change the behavior?

Any help appreciated,

Thanks.

 

3 Replies

  • What video drivers are you using, AMD?  You need to look for something called “dialog box positioning” in Hydravision, then set it to center dialog where mouse curser is located.
     
    Can be a pain to get working though, especially if switching between Windows desktop and DeltaV desktop.
    From: DVUser007 [mailto:bounce-DVUser007@community.emerson.com]
    Sent: Wednesday, June 04, 2014 3:49 PM
    To: DeltaV@community.emerson.com
    Subject: [EE365 DeltaV Track] Multimonitor Pop-up Position
     

    Hi,

    I have a quad monitor V9.3 system, can anyone help with the way to set the position of the pop-ups?

    The faceplates & detail displays work as expected and pop up in the last position everything OK. It is the operator set-point data input fields which pop up a dialogue box, always appear on the primary display rather then the display they have been clicked on.

    The pop-ups are generated via an "on click" script which runs the following procedure: GetPBLFormAlphaNum

    Is there a setting somewhere I am missing to change the behavior?

    Any help appreciated,

    Thanks.

     

  • In reply to AdrianOffield:

    See: NK-1100-1054

    :)

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to AdrianOffield:

    Thanks AdrianOffield, Hydravision was the culprit. :-)