Parameter for all alarms

I am looking for the parameter that would give me a status of true if any alarm (hi, low, module, etc) were to come in on a module.

  • Use  MODULE/ALARMS[1].CUALM

    The [1] is for the index of the highest priority alarm.  CUALM is the current alarm state.

    www3.emersonprocess.com/.../r_thealarmsparameter.html

  • In reply to Youssef.El-Bahtimy:

    Thanks. If the highest priority goes away and the next priority comes in. Will the module still show true?

  • Yes. The array will shift [2] to [1], [3] to [2] etc.

     