I am looking for some help building SIS faceplates that will allow information to be retrieved below the module level, to a composite block. Currently my standard faceplates retrieve information only at the module level.
Where a search on module 'hazard detector' "XX1234" will call the module faceplate for module XX1234.
White I am hoping to do is to build a faceplate where i am looking for a particular function block within the module.
In this case, I'm calling for 'builing x' hazard detector XX1234' where the module is 'building x' and the composite block is 'hazard detector xx1234'
Instead of an DVSYS.@MOD@ call, i'm attempting to set up an DVSYS.@MOD@/@COMPOSITEBLOCK@ call.
Any help would be greatly appreciated..thanks!
Hi randy,
Mostly if you have gone through the SLS training EMERSON encourages you to use only SIS Dynamos and face plates as these are made for SLS.
Integrating a SIS faceplate into a PCS faceplate is quite difficult. I tried to do this in a project but failed.
Later on i made a separate screen with SIS dynamos. You can make a separate screen for the SIS or for the composites like Bypass or C&E screen.
Regards
Asim