Is there a way of changing a "Reverse Acting" PID loop to "Direct Acting" in runtime?
I tried to write the values for above "16768" and "17792" using calc block but PID block was not happy and did not change the action
Shoaib
You have to put the target mode of PID block to Out of Service, then write your value, and then return the PID block to the mode required.
Regards,
Matt
Is there a way of changing a "Reverse Acting" PID loop to "Direct Acting" in runtime? I tried to write the values for above "16768" and "17792" using calc block but PID block was not happy and did not change the action
In reply to gamella:
See this previous post about Reverse/Direct changing and the way to do this.
community.emerson.com/.../5250.aspx