Hi Guys,
I tried searching this site, BOL and the internet. no luck.
I would like to be able to have two instances of a faceplate open at the same time. I want to view the PID faceplate of two loops at the same time (each loop would provide data to 'its' instance of a PID faceplate. Is this possible/easy?? If so, how would I go about it?
Cheers,
Eric
1. Edit the script in usersettings.grf. You need to uncomment a line to enable multiple faceplates and to set the maximum number.
2. Run the update popup pictures utility in DeltaV Operate. This is a button that looks kind of like a faceplate and is located on the DeltaV Utilities toolbar.