Anyone know why I can not delete some points in the history collection of a certain module? We are running Ver 11.3 and when I go into the modules history collection and try to delete some points I was recording is says an error has occured and gives me no reason.
Is your module part of a class?
In reply to Travis Neale:
I would have to say no. I am not sure what that really means kind of new at this doing the learn as you go stuff.
In reply to Bill Sayers:
Did you made this module by copying other modules? or making it classless & changing something in it?
Can you modify other things in the module & only history collection is giving error?
Such errors occur sometimes, if the database has some ambiguities or disconnections in background.
Try to export the module. Delete the complete module & reimport. This generally resolves any such issues.
In reply to amodbobade:
Well not sure why but I was able to delete the history collection in DeltaV Explore but not in Control Studio for that module. Don't know if its a bug in ver 11.3 or not. I was able to modify other things in the module and I don't recall if I had copied it or not from other modules.