Alarm banner module faceplate not showing up when clicking on it

I have the area assigned to the correct node, and in the alarm banner I have the button enabled for Direct Access to the faceplates, but I don't know why when I click on an individual module in the banner, it's faceplate won't pop up. The station I am using was also downloaded. DeltaV Live Premium License: Basic is loaded on the station.

3 Replies

  • Can you open the module FP from tool bar by clicking the FP button and typing in that tag?
    Does the module have a defined FP in Module Properties?
  • In reply to Matt Stoner:

    Yes, I am able to search and open the FP for the module
  • In reply to rhamlin:

    It's been along time since I've looked at that logic in the alarm banner but it was pretty simplistic but uses a monitor variable if I remember correctly. Wonder if it is opening on a monitor/position you can't see?

    You may have to log a call with GSC on this as it is pretty difficult to troubleshoot this issue in a forum.