Hello to all, I just needed some help regarding the CHARM IOs assignment to a controller.
Here's the setup:
I have CIOC-02 assigned to CTLR-01 and the CHARMS in it are all assigned to CTLR-01 (it has CHARM Baseplates 1 to 4). Now, we have added CHARM Baseplate 5 & 6 for a new project but this is in a different Line (We have Line 2,3 & 4). We wanted to assign the CHARM IOs in baseplate 5 & 6 to CTLR-02 (another controller). Is it possible or ok to do that even though the main CIOC-02 is only assigned to CTLR-01?
We have 2 CIOCs that are assigned to both CTLR-01 & CTLR-02, do I have to that as well to CIOC-02 to avoid issues? Thank you in advance.
In reply to Jesse Delanoy:
Andre Dicaire
In reply to Andre Dicaire:
This is the controller performance index we have in CTLR-01 (SX)
While this is our CTLR-02 (SQ)
In reply to Douglas Crowder:
In reply to dolatrec:
Hello Andre,
It is total. Yeah some of the modules we tried to reduce the module execution rate like the temperature monitoring to 3-5 seconds those that are not critical, and we tried to avoid as much as possible inter controller communications and making sure there's no unresolved ref. CTRL-01 is SX while CTRL-02 is SQ. We do have a plan to change SQ to SX this coming October 2024 to increase the capacity because we are adding another production line. Line 2/3 in CTRL-01 and Line 4/5 in CTRL-02, actually they are in simplex right now so we are also making it redundant.
We checked the Assigned IO under controller and there are CIOCs assigned to CTRL-01 than CTLR-02
Here's our IO license demand