Hello and Happy New Years,
Over the last while we have been having issues with one of our EIOC's getting an EVENT_LIMITED. state and Inputs Transfer Failure description. From what I can see nothing has changed in our system to cause more loading on the network. I saw in one post regarding VIM2 cards that it has to do with the Pro+ receiving to many events.
Can anyone explain in more detail the relationship between the Pro+ receiving too many events and the EVENT_LIMITED state?
What could cause this issue and is it more likely to be on the EIOC side or PRO+ side?
We are on DeltaV 13.3.1. The performance index for the EIOC says 5.0. There are 46 device connections using Modbus TCP. There are 239 modules. Going back in the history I see several of the modules have had this issue come up briefly every couple days. However, on the 23rd and the 29th of December we had 2 times where the group of modules associated with our mill drives go into this state. All 4 drives had this issue for a couple hours on both dates and it is the first time we have seen it. When I looked at a trend in PHV for an analog value it was still being read, so data is coming but maybe 5 times a minute we would enter the EVENT_LIMITED state.
Thank you for your time,
Michael Sovereign
Link to VIM2 discussion about EVENT_LIMITED