Hello Everyone,
What actually happens if we download a phase to a redundant controller while it's running?
DeltaV gives a warning: continuing with the download wil cause the phase not to be updated on the standby controller. What does this mean?
1. If there is a switchover while the phase is still running, the old version of the phase will be running (not a big deal), but if the phase unloads and loads again, it will have the new version on both controllers.
2. The standby controller is not updated to the new version at all, so it will always have the old version of the phase. We need a second download, while the phase is not running, to ensure the standby is also updated.