Restricting alarm shelving in DeltaV 13.3.1

We would like to control access to shelving of alarms, preventing shelving for some and only allowing certain users to shelve others. I appreciate that shelving is controlled by which lock the field .OPSUP is assigned to. The obvious solution is to give users access to the key for this lock only in certain areas and then assign the alarms which they can suppress to this area. However we already have a complicated area system for access to different plants. Is there another way?

I found that if the suppression timer limit is set to 0 then the alarm cannot be shelved (or at least it is shelved then immediately unshelved). This would prevent shelving entirely but wouldn't allow differentiation between users.

5 Replies

  • I'm wondering if you could benefit from one of the AgileOps applicatinos like List Management

    This gives you independent levels of control for alarm management rather than attempting to configure the DCS logic.  

    There is also the Dynamic Alarm Management module that can implement State based alarming 

    As for handling this in DeltaV, you could create a module that manages suppression, abstracting out the alarms that can or cannot be suppressed.  A module can write to the OPSUP and SUMTMO fields of another module.  This would allow all modules to remain in their current plant areas, but give you a new module you could place in a new Plant Area and restrict access to it, and remove access to OPSUP in all other areas.  This could get complicated really fast, so I don't know if this is viable.  Just a thought.

    Maybe you could add some signature policies that require confirmation in order to suppress certain alarms. If OPSUP requires a supervisor and only some Operators have that privilege, maybe that lets you control who can suppress and who cannot.

    Personally, I like the idea of the AgileOps Alarm management layer.  This allows you to separate alarm management functions from control module logic.  The people managing alarms can implement strategies that do not require control module changes and downloads.  It provides a clean break in responsibilities.  Although Alarms are appropriately executed in the controller where they are time stamped and are universally reported to all consoles from one source, the suppression and operator management of alarms makes  more sense to be managed above the controllers.  

    Andre Dicaire

  • Cedric, we had the same issue at our site.

    We define certain alarms to be critical and these are not allowed to be suppressed by an operator.

    We have an administrative process to allow a supervisor to enable shelving.

    The way we manage this in DeltaV is the SUPTMO is set to 0 for all of our critical alarms.

    We added a Suppression Enable column to our PCSD detail display adjacent to the Suppression column on the alarms Tab.

    If the user has supervisor credentials, he can enable a check box. Enabling the check box sets the SUPTMO to our default of 4 hours.

    The status of the check box follows the SUPTMO, that is: its "checked" if the SUPTMO is > 0 and non-check if = 0.

    This has been working well for us. If you want more detail, look for me on linked in and I can share some images etc.,

    Mark Hymel
  • In reply to MPHymel:

    Here is a pic of the detail alarm tab mentioned above

  • In reply to Andre Dicaire:

    Thanks Andre for your reply.

    The Agile Ops does look very comprehensive but is probably a bit expensive and complicated for what is a relatively small installation.

    I have used the idea of 'indirect writing' via another module to solve other security issues but as you say this might get very complicated if there are a lot of alarms.

    Electronic signatures looks interesting. I haven't used this. Does it require a licence or just enabling? I think the problem may be that this is also area based.

    Andrew Chadwick
  • In reply to MPHymel:

    Thanks Mark for your interest and reply.

    I did find your previous conversation on this topic back in June 2020 and your approach sounds promising.

    Regarding the additional checkbox, presumably when it is unchecked SUPTMO is set back to zero. Presumably the supervisor must remember to uncheck the box when shelving needs to be restricted again? Or is there some automatic method?

    Andrew Chadwick