I'm working on designing a system and my team is debating the virtue of using a sub-system Allen Bradley PLC for a particular plant area. The proposal was to use a VIM to integrate the AB-PLC.
I'm pretty ignorant of VIM's, I only really know what they are, but not much about their capabilities. (PS- Just read the Mynah documentation for one of their products- doesn't look like this would be possible???)
Does anyone know, at a minimum, if AMS can use the DeltaV interface through a VIM to communicate via HART with devices on a PLC Sub-network. Has anyone ever done this?
Thanks for your input.
Brian
Brian McWhorter ISA:CAP OPC:SI PE:CSE
I'm not super familiar with AB - is the HART data available to the PLC?
If so, I don't see why you couldn't map it into registers for DeltaV. If not, you could always strip off the HART signals with a multiplexer and pass them to AMS that way.
Brian - In essence, the VIM acts like 4qty DeltaV serial cards. If you have the HART variables mapped to your PLC's memory registers, you can pass those to DeltaV as floating point values, integers, etc... AMS will not be able to manage your assets through the VIM, as these are "just numbers" coming across an Ethernet/IP or MODBUS network (depending on the driver you purchase). As Aaron said, you'd need a multiplexer to pass the HART signals to another network layer to get the signals up to AMS.
In reply to Ray Emerson:
i am not sure, but maybe exist different way...
Try to ask AB for solution to "extract" HART data from PLCs ( maybe they have any solution ) with interface to OPC or any kind of "Ethernet" ( try to ask for any "trial version" for testing ). After that you can try to check implemention possibilty into AMS DM ( in case of OPC interface you will need special licence, in case of ethernet I guess only "extended" interface - cheap ). In case of multiplex solution it should be expensive ( especially in case of "present" wiring ). How many HART devices do you have?
There exist also second possibility - wireless THUM adapter embeded directly on instruments ( HART data will be connected to AMS DM thru thsi way ).
Than possibility exists - try to check and calculate possibility / price.
Brian,
As far as I know there would be no way for AMS to "see" any HART devices through the VIM. There are positives and negatives to using a VIM.
The VIM uses either Modbus TCP or Ethernet I/P and you are restricted to landing your data in DeltaV landing modules just as you would with a DeltaV serial interface. In fact the VIM will show up in DeltaV explorer as multiple serial cards.
If you need to interface to a PLC then the VIM is definitely the preferred approach but you will lose any ability to communicate to smart devices with AMS. If there are a significant number of HART/AMS/Profibus DP devices and you need to use AMS then you've only got two real opitons; 1) use HART multiplexers for the devices under the PLC and "bypass" DeltaV to commuicate with AMS. 2) omit the PLC all together, run the logic in DeltaV and have full AMS access to all devices.
hope this helps,
dewey
In reply to Dewey Kuchle:
Adding on to Dewey's reply
If the AB PLC is Contrologix with specific HART cards, AMS could interface directly to it for HART devices. It requires Spectrum Connects software. The best solution would be AMS via DeltaV (for HART, DP, and FF) but this is an option for HAR Tonly.
Just wanted to write and close this out. I appreciate the responses from all the participants.
I was steered in a good direction and was able to do some investigation that set me at some ease.
Thanks to all... Brian