DeltaV Operate multiple screen

Hello everyone

I would like you to help me with an issue regarding licenses for deltav operate and quad monitor setup, if you allow me.

I currently work with deltav v12, in the pro plus station we have 4 screens, but deltav operate gives a message saying it's not licensed for 4 screens and then closes. I have a cd for quad monitor license but honestly i'm new to this and don't know hot to install the license to use all 4 monitors at once. The solution for now is unplug 3 of them and use operate with the remaining screen, and then re-plug the 3 screens when I don't need to work in operate.

Any help will be appreciated. Many thanks in advance.

Julian.

1 Reply

  • First you need to load the license, Do this from DeltaV Explorer by clicking menu option File->Licensing->Load License File and browse to where license file is located.

    After the license has been loaded you would assign the Quad Monitor license to the workstation you are trying to use 4 monitors. Click on Licenses under System Configuration->Setup, find a Quad Monitor license, right click, select assign and pick the workstation name.