Bulk edit import ' character inserted in expression fields.

Hello,

When i try to reimport a module thru Bulk Import,  (motor) DeltaV Explorer 11.3 inserts " ' " character in expressions.

So instead "  '//H1160/DI1/OUT_D.CV' = 0" i have " ''//H1160/DI1/OUT_D.CV' = 0".

What is wrong? Could someone explain?

8 Replies

  • Nobody Knows how to fix this bug? This is a DeltaV Bug, is there a KBA about this?
    What can be done to make the tool of DeltaV Bulk edit to run properly? To stop the Bulk edit from inserting in expressions field "apostrophe " character?
  • In reply to stamate_mircea:

    Hello,

    I believe KBA NK-1100-0171 describes the behavior that you are seeing.
  • In reply to kmarks:

    Thank you for response,
    KBA NK-1100-0171 indeed is the one i am looking for, but there is specified :

    "Resolution:
    Please refer to KBA: AK-1000-0065: DeltaV v11.3 Software Updates. Follow the link for Incident TFS34116 to download the hotfix, which can either be in the form of a standalone hotfix or part of a hotfix bundle."

    At TFS34116 there is no download link
    "For more information, refer to KBA NK-1100-0171: Parse Error in Expressions with External Reference Parameters in Function Blocks During User Defined Import. "

    By any chance somebody has the appropriate hotfix from emerson to fix this issue?
  • In reply to stamate_mircea:

    That item was fixed by Hotfix: DeltaV_113_WS_04_CSS since it is listed under that section but is superceeded by many other hotfixes with DeltaV_113_WS_11_CSS being the last update.

    Download this from the bottom of the KBA.
  • In reply to Matt Stoner:

    I could only found the link for DeltaV_113_WS_04_CSS.zip that does not work. This mentioned by you: DeltaV_113_WS_11_CSS in what kba can be found?
  • In reply to stamate_mircea:

    Sorry I had opened an older version of this KBA, The latest version was published on 05 Sept 17 and the download is on page 4 under section 1.2 of the KBA pdf file.
  • In reply to Matt Stoner:

    Can you tell me the KBA name? It is NK-1100-0171 from the date of 05 Sept 17?
  • In reply to stamate_mircea:

    It is the KBA in your earlier post with the Resolution, "Please refer to KBA: AK-1000-0065: DeltaV v11.3 Software Updates"