HI
I am studying the feasibility of converting a manual valve to a motor operated one.
Any suggestions please, from practical experience.
Thank you,
John,
from the valve perspective you should also consider,
- valve Maximum Admissible Stem Torque/Trust (MAST)
- stroking speed design limitation
- valve packing original design (how often now will you operate the valve?)
- valve Top Mounting, maybe you will need for an additional std flange
Anyhow it really depends from the kind of valve you have installed and the related expected service.
Feel free to contact me to discuss further.
Regards,
Paolo Tomaini | Sales & Development Manager | Power & Steam Europe | Final Control
Emerson Automation Solutions | via Castellanza 47 | Rescaldina (MI) | Italy
T +39 0331 575 270 | Paolo.Tomaini@emerson.com | http://www.emerson.com