Hello,
Does anyone have experience using the 3051S DP pressure transmitter together with the 1199 seal diaphragm system in cryogenic applications?
I am considering using this type of solution for level measurement in cryogenic service when compared with a traditional 3051S differential pressure and purge system installation.
Best Regards.
Hi Cristobal,
Cryogenic liquids are too cold to measure by direct contact with a remote seal or pressure transmitter. Impulse piping is used to allow the liquid to vaporize into a gas and the warmer gas is allowed to contact the sensing element.
If you would like to use remote seals, you can enter information about your application in Instrument Toolkit to determine the Total System Error.
https://www.emerson.com/en-us/automation/brands/rosemount/about-sizing-and-selection-tools
Cryogenics Level.pdf