Dear Sirs,
I have question about accuracy, hope someone can help to figure it out.
What side is right that I should use?
Ex. 3051CD1, accuracy: 0.1% of span, For span less than 15:1, (0.025+0.005(URL/span))% of span.
2. Turndown Ratio:1, URL/span=1, accuracy should be the highest, but Sensitivity is the worst (like right side 0.635mmH2O).
3.For Spans less than 15:1, (0.025+0.005 (URL/span))% of span, meaning turn down ratio is not greater than 15, so formulas are used in Turn down Ratio=<15, so the span should be greater than URL/15=42 mmH2O when using this formula (left form).