751 Remote Transmitter

Hi, can someone advise me what the load for 751 remote transmitter and a 3051S DP transmitter ? I need to calculate how many 751 remote transmitter i can install in a 4-20mA loop. Requirement calls for 1 x 3051S DP flow transmitter and 4 remote indicator. Can i design all transmitter in series in the same wiring loop considering the distance of 500 meters from the control room ? 

Appreciate if someone can advise on this. Thanks. :) 

  • What method of hazardous area protection is required (if any)? Is your power supply a nominal 24V DC or some other value?
  • In reply to Leon Trunecka:

    Hello Jonathan,

    I received this response from level specialist, Brian Sorenson, via email but will share for him until he and his team are able to join the community. :)

    Each 751 will add less than 10 ohms loop resistance in the loop and if the displays were removed or damaged, the current would go through the diode and drop the voltage by 0.7 volts for each 751. Worst case would a 2.8 vdc voltage drop counting all 4 remote indicators. Basically you just need to keep at least 10.5 vdc at the transmitters terminals to keep the transmitter powered. Max output of the transmitter should be considered 23 mA. You could multiply this x loop resistance to get your total voltage drop and subtract from the power supply voltage.

    Brian Sorenson

    Best Regards,

    Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast

  • In reply to Rachelle McWright:

    Hi Leon : It's located in Zone 1 and 24VDC power supply.

    Hi Rachelle/Brian : Thanks for the help and reply. It helps and i'm pretty clear on this. Just to go a bit further on this, can i check if this concept is the same if i connect the 751 onto the test terminals of the 3051S, i.e. connect in parallel instead of series.

    Once again, thank you so much for the replies.
  • In reply to Jonathan Tan:

    Additional information from Brian:

    Multiple 751 Field Signal Indicators cannot be wired in parallel by using the test terminals, because the diode in the transmitter terminal block will be biased and current would flow through the diode instead of through the 751 indicators. Multiple 751 indicators would have to be wired in series with the transmitter.

    Best Regards,