Hi all,
Has any used a Siemens PN/PN coupler to communicate with a Delta-V Ver 13 system?
we are having a packaged plant delivered to site and it is controller by a Siemens S7-1500 CPU, the supplier of the equipment has a PN/PN coupler to allow data to be transferred to/from our system, but I am wondering what hardware on the Delta-V end I would need and what is the recommended paractise do i need a VIM for example?
Any advice here would be greatly appreciated as in the past we have either used a serial link (which is not available) to communicate with other PLC's on the ste.
Thanks
GaryL
Hi GaryL,
You might want to reach out to New England Control (neci.com) for help to identify the right solution for this integration using the coupler. NECI is an Emerson Impact Partner that can support you in New England area.
I would look at using the Emerson DeltaV S-series Virtual I/O Module 2 to connect to the PN/PN coupler. the VIM2 has the capability to connect to PROFINET data exchange to DeltaV but I don't know if this the solution for what you need. The other option is if the PN/PN Coupler can transpose the PROFINET device data into Serial data then you will be able to send that data into the DeltaV system using their Serial Card or VIM.
Here is the link for S-series Virtual I/O Module 2 product datasheet (VIM2):
chrome-extension://efaidnbmnnnibpcajpcglclefindmkaj/viewer.html?pdfurl=https%3A%2F%2Fwww.emerson.com%2Fdocuments%2Fautomation%2Fproduct-data-sheet-s-series-virtual-i-o-module-2-deltav-en-57730.pdf&clen=806077&chunk=true
Hope this helps,
Tinh
In reply to Tinh Phan:
In reply to GaryL:
In reply to RobPerry:
In reply to Chris Dahl:
I have confirmed VIM works as IO controller to a PLC setup with I-Device function. Basically, you configure the Project like in this safety plc example "across projects", where you create a dummy PLC/network, create transfer areas, delete dummy PLC, compile, export GSD, Load, and do the vim config. Also, make sure to use addresses outside of typical hardware addressable space. I was getting issues on PLC project when I was using lower address numbers (even when they weren't assigned to hardware). I-device setup will work as long as PLC supports it and the PLC/VIM are in same subnet. Otherwise, the PN/PN coupler is required. The I-device setup is arguably simpler on both TIA Portal and vimnet vs PN/PN coupler. I would recommend it if device supports it.
https://cache.industry.siemens.com/dl/files/798/109478798/att_992839/v2/109478798_config_idevice_safety_DOC_V22_en.pdf