We have a Rosemount 1420 Wireless gateway commissioned in the last year. We have had two instances where all our wireless instruments stopped updating and went to MODBAD status for about 8 minutes before starting to work again. We cannot find anything that is causing this to happen. Is there something we should be looking at?
In reply to John Rezabek:
In reply to Glenn Faber:
The fact that all the connected devices go from NaN -> okay more-or-less at once (right?) makes me think you're seeing an issues with DeltaV connection to the Gateway versus a wireless issue. But maybe the intermittent bandwidth intrusion described by @mco_exchg looks similar, i.e. the mesh doesn't need to "rebuild" just because a box truck parked in front of it. Is there any fiber / media converter or other intervening switch / firewall / router between the DeltaV switches and the gateway? Are any such appliances "shared" in some way by both primary & secondary PCN?