Hi
I have a problem with the OAR composite in a phase when I set the ACTION as Continue, with a default response (DEFAULT) after timeout (TIME).
e.g.
TYPE = INT no limits
ACTION = Continue
DEFAULT = 2
VERIFY = None
TIME = 60
This works fine when the phase is run from the unit faceplate but does not work when the phase is run from the BOI.
When the phase is run from the BOI the DEFAULT is not copied to the INPUT and the OAR does not reset.
Is this a known issue with the composite? Has anyone found a work around?
Many thanks
Colm
In reply to vmvmhatre:
Thanks for your response. If you have time please look at screenshots below..
1. Setup with 30s timer. Default answer = 20.
2. 30s expired. Type not reset to None. Input not equal to default in first screenshot.
Please let me know what you think.
I have tracked REQUEST in Watchit. After the 30s the Request value is 6000, 10, 0, 3201.
In reply to Colm Crowley: