Clarification for Loop Current Disparity Error for HART

For the HART_ERRORS , I have not had luck in finding what % or value of deviation between digital and analog values triggers the Loop Current Disparity Error.

Hoping someone in the group may have that info.

Appreciate it

3 Replies

  • Loop (analog) current is compared with digital valure read using HART command - it has to be within -/+ 5% of signal span and has to fail twice before it gets sets.
  • In reply to Lun.Raznik:

    We saw this before on analog signals that are so noisy that the HART value could never "keep up" and match. We turn off analog disparity in such cases.
  • In reply to Lun.Raznik:

    Appreciate it, I just could not find this :) Though there is always a little error between digital value(mostly also on local display) and the analog value as read into deltav, hopefully this will help identify possible failures.