• Not Answered

SIS TECHNICAL CLARIFICATION

Dear All,

Good day.

Myself Venkatesh Jayabalan have been working with Emerson Deltav & Ovation DCS. Currently i am working  Qarnalam steam project in Oman with Sevenseas Petroleum LLC who is LBP of Emerson. I would like to post a question that when exporting SIS Database  through bulk edit is it possible to export the SIS tag list as i need to know SIS tags parameters such as "Trip limit", "Trip delay", "Detection type" etc.. for the complete SIS exisitng database and I have tried through bulk edit but it is not allowing me to do. Do we have any separate tool to do that or we can do it normally.


Could somebody get a solution for me on this above regard.

thanks in advance

1 Reply