Hello All,
I read several other posts related to this question, but they were old (2014, 2015 i think). Has anything changed in DeltaV that allows the order of module execution to be forced to a particular order?
In reply to vmvmhatre:
Thank you for confirming that no new features have been added to enable this
In reply to Brian Hrankowsky:
In reply to Lun.Raznik:
The only way I'm aware of that execution order of modules can be assured is to have the modules being manipulated embedded in the module doing the orchestration. The picture below is conceptual only, not meant to be a solution to your problem but does show execution order control of other control modules. You could add an off delay of the valve executing first to delay it closing for a scan just prior to the "bad path" valve opening when transitioning back to bad quality.
In reply to Scott Thompson:
Andre Dicaire
In reply to Andre Dicaire: