We are running 11.3.1. We use tool tips to give information on a few tags that are not clickable. The tool tips is a great feature to do this, however the tool tip does not remain visible for very long. The tool tip pops up as the mouse cursor hovers on the tag but the tool tip quickly goes away. It stays visible for less than one second. is there any way to make the tool tips remain visible longer? Thanks for any help.
I believe if you open the property window in DeltaV Operate - Edit mode there is a time setting for the tool tip display time.