Hey guys,
I'm working on expanding a system by adding 8 additional bath class-based unit modules. I think I'll need the appropriate amount of VE31UPSxxx licenses, but do I also need the appropriate number of VE22UPSxxx licenses? I'm trying to figure out the difference between the two types of licenses and if both are required.
You only need the VE31UPSxxx license if you have EMs and/or Modules placed below class based Units (similar to pic below)
You need the VE22UPSxxx license for the Batch Units that will be running in the Batch Executive (located under a Process Cell Class)
You can reference the below datasheets for more information (Note: the VE22 licenses depends on the level of batch you have):
https://www.emerson.com/documents/automation/advanced-unit-management-software-en-57598.pdfhttps://www.emerson.com/documents/automation/deltav-basic-batch-en-57600.pdfhttps://www.emerson.com/documents/automation/deltav-advanced-batch-en-56204.pdfhttps://www.emerson.com/documents/automation/deltav-professional-batch-en-56206.pdf