Hi
I have deltav ver 13 , SQ controller and I have s series serial card, configured for RTU , Master. On micrologix1400 end I have 1761-NET AIC+ serial to rs 485 converter and wiring is regular A, B and GND, A is connected to serial card terminal 10, B is connected to serial card terminal 12 and GND is connected to serial card terminal 9.
I added device in explorer but it is not communicating, when I try to diagnose it shows bad device and not communicating I have only 1 device connected serial card and distance is not more than 30 FT.
I tried with different baud rate but no luck.
my serial card LED light is off even though there is only one device in line.
below is screen shot of diagnostics.
please help me to solve this error.