Hi Everyone,
I was trying to change the outscale of a PID block using the ACT(IND=1). When PID block IN input is not connected then i am able to change the outscale. But when i will connect IN the input to the PID , ACT( Action block) shows an output error & outscale come to default values.
Action Block syntax i have written is( '/PID/out_scale.EU100':='//FIC-1558/AI1/Out.CV)
Thank you,
In reply to gamella:
I am using this for RCAS mode. When i keep Target mode Auto & normal mode Man then outscale range works well('/PID/out_scale.EU100':='//FIC-1558/AI1/Out.CV) as i required. This is because in control option there is one option (No out limits in manual). When i changes the normal mode to auto or Rcas outscale freeze to its last value. Is there any way to write no out limits for RCAS & Auto mode.
In reply to Rajeev Kumar:
In reply to Matt Stoner: