Hi
in Deltav 11.3.1 , when I click on Tag search utility button, show error " type mismatch" Error number 13 (D), after accept error meesage,, pop up picture open and search utility works but only show some of tags.
I only migrate database and import it in deltav explorer.
Thanks in advance
In reply to Matt Stoner:
To add to what Matt has said, an easy way to search for them is to look through the file that's downloaded to the workstations that the tag lookup table is pulled from. You will want to use caution as you do not want to make any changes to this file, but it makes it easy to search for bad characters. The file is the module table file (MODT.SCR in the \DVData\download\ directory) This file can be looked at in notepad and if it is an apostrophe causing issues, if you search for ''' (three apostrophes in a row), it will usually find the correct line. Earlier on the line will point to the module in question. Another common thing that can happen is during a bulk edit, it is possible to import a carriage return at the end of a line of any of the faceplate, detail, pcd or description files. This is not immediately visible in explorer, but if you select the end of the line and hit the left arrow and the cursor does not appear to move, it could be the culprit. These are really only found searching through the module table mentioned earlier. In the screenshot, you can see the two different cases that can cause the error message. In both cases, you should go back to explorer to correct and redownload and see if the error has resolved itself.
In reply to MOH:
In reply to Matt Forbis:
I couldn't get the picture to show up in the first post I had.