DeltaV Configuration for integration with IM 155-6 DP HF

Hi everyone,

Is anyone familiar with .configuration of these devices

IM 155-6 DP HF (version 3.1 gsd)

Communications are established & there is is some data exchange.

However, LED status of the Siemens remote IO indicates a parameterisation / configuration.

All appears fine on DeltaV side until I enable 'Configuration Control' parameter which then brings up a configuration fault & data exchange stops.

Regards

John

1 Reply

  • one further update
    I just got my PLC engineer to hook up an S7 to the IO - it worked fine. When the DeltaV was reconnected, it actually cleared all errors. But once the IO station was power cycled, the error returned