Hello,
Today I attempt to tune a flow loop that is normally set in AUTO.
When I place the loop in MAN to stabilize the flow before step change, I notice the PV (actually flow) was still oscillating and not stable. Normally when I place a loop in MAN, the valve is constant output and PV stays stable.
I believe, I need to check the flow meter for issues and make sure the valve is not moving.
Has this happen to you before?
Thanks,
In reply to leirbag:
leirbag said:1. Check first if your flow is single in the line (there is no other flow from the same pipe). 2. Check if there is no other control element (automatic or manual) on the line. 3. Check the flowmeter and increase the damping time (more than 2-3 sec) if necessary.4. Check the control valve if oscillating due to mechanical problems, positioner malfunction problems or booster relay gain problems (if booster relay exist).
Thank you leirbag for response. I will definitely check the steps above before tuning.
How does damping time effect the flow measurement?
In reply to DCS Newbie:
leirbag said:The traditional signal filtering method for getting a stable output in noisy applications is to add damping time. Emerson magmeter transmitter default damping time is 2 sec. While this makes the output look stable, the flowmeter’s response time to actual process changes is compromised, if this constant is very high. I sometimes use such constant up to 10 sec. This is a decision to be taken only when there is a disturbing factor in the process that produces those sudden swings in flow.
Thank you Ieirbag,
How does damping time in the transmitter relates to the PV Filter? Does this mean the actual flow measurement can be damp on the DCS side as well?
Thank you for help.