I have a Fluenta flow meter, we are bringing in hart communication to a AI charm. I have 4 separate modules, one for each value. Three of them are working great using HART_SV, HART_TV & HART_FV & have good status. The forth one that is configured to use HART_PV and is updating in the AI block to the correct value. However the status is BAD. I have cleared all the masks for status for both the AI block & the module. All of the AI modules are set for direct independent. I have re-assigned the HART_PV to different modules and the error moves with it. The vendor has to come out to set what is assigned to the one hart enabled channel, and unfortunately the current assignement in HART is correct but the 4-20mA is not. That is why I am not just using the %field value. Anybody have any recommendations on where to go from here to clear the status? Thanks....JWB